I am having issues with a card reader in my elevator not sending wiegand data to my controller. all voltages are good at the reader. think it may be interference causing problems. will a wiegand extender fix this issue?
I used to work for an access control manufacturer and a wiegand extender was always recommended when interference was present. Another option that I've seen work well in the field is a unit now made by Schlage (or IR or whatever):
Use shielded wire, which is metal foil wrapped around the outside of the cable. This keeps outside electrical noise out. Ground one end of the metal foil.
Then there is "voltage drop" with long distances. Use a larger gauge wire for long distances. Something which starts out as 5 volts on one end can be
Does the reader travel with lift or is it at a floor for access? A lot of interferecne has been known to be in the traveler cables of some MFRs elevator. An extender may or may not work, that would depend on the tolerance of the receiver of the weigand signal.
the reader is in the elevator car. the problem i am having is finding an extender that will work with 18/2 wire with overall shield. all the manufacturers extenders that i can find spec out twisted pair wire, I think most of them convert the wiegand to 485 then back to wiegand at receiving end.
what settings would i set up hyper-terminal for? I would assume that is dependant on the wiegand format? I am using paradox R885 readers with 26 bit weigand format.
It's impossible to answer that question without further troubleshooting.
Have you used a program like Hyper-terminal to check the data string at the controller end?
I was just going by one install I did where 12 of the 36 readers would not read a card correctly and they all happened to be the readers that were farthest away. Our tech guru at our office said to put some pull up resistors between the power and Data 0 and power and Data 1 lines at the panel. Every reader was working after that.
I just happen to be going by the site tomorrow morning for remodel work, I'll look at the resistor value. It's been 3 years since I did it. It is a Lenel system with the Indala readers.
Gonna say it's either 1K or 4.7K resistors. I'll look when I get there and post tomorrow.
I was just going by one install I did where 12 of the 36 readers would not read a card correctly and they all happened to be the readers that were farthest away. Our tech guru at our office said to put some pull up resistors between the power and Data 0 and power and Data 1 lines at the panel. Every reader was working after that.
I just happen to be going by the site tomorrow morning for remodel work, I'll look at the resistor value. It's been 3 years since I did it. It is a Lenel system with the Indala readers.
Gonna say it's either 1K or 4.7K resistors. I'll look when I get there and post tomorrow.
I was just going by one install I did where 12 of the 36 readers would not read a card correctly and they all happened to be the readers that were farthest away. Our tech guru at our office said to put some pull up resistors between the power and Data 0 and power and Data 1 lines at the panel. Every reader was working after that.
I just happen to be going by the site tomorrow morning for remodel work, I'll look at the resistor value. It's been 3 years since I did it. It is a Lenel system with the Indala readers.
Gonna say it's either 1K or 4.7K resistors. I'll look when I get there and post tomorrow.
cool, I am going to my site today, will try out some different resistor values
Usually set the baud rate at 9600 and leave the rest of the settings default.Hyper terminal is great for determining that the data is being sent properly before you start chasing ghosts. Kinda makes you regret tossing those old windows 95 laptops with the serial port among other reasons