I installed this thing years ago, then had some trouble with it, so I left it dormant.
I'm trying to get it up and running again. Most things seem to work, but I'm having trouble with 2 items.
-4 wire smoke detectors. I have 4 ESL 449CT detectors with a DSC RM-1C power supervision relay at EOL. The 5600 resistor is installed, too. The problem is that the loop is not powering up. I've hooked positive to Aux+ as recommended, and hooked negative to PGM2. I get no power. I put a multimeter on the contacts and it confirms no power. I'm also getting a wiring fault on zone 7 (I've designated it as delayed Fire) I removed the power supervision unit and hooked the detectors up to Aux+ and Aux- and the loop powers up fine. I get the LED blink every 9 seconds from the detectors as normal. I accidentally put the power supervision unit back on the EOL while still hooked to Aux+ and Aux-. The system worked for ~7 seconds and the system went off. I disconnected the power supervision unit, unplugged the system, disconnected the battery, then re-atached power. Everything came back up fine. Since I know that Aux+ is working, it must be an issue with PGM2. Is this a programming issue and PGM 2 just isn't activated? Secondly, I've designated zones 5 and 6 to be interior zones (beams) I don't want them activated during 'Stay' mode. But, when I hold 'Stay' down to activate it, it runs a system test. (??) How do I get this key back and working the way it should?
TIA,
Dave