Newsgroups: alt.security.alarms From: "Rafi Hecht" - Find messages by this author Date: 31 Aug 2005 06:35:04 -0700 Local: Wed, Aug 31 2005 9:35 am Subject: Keri Doors 4.3 Reply | Reply to Author | Forward | Print | Individual Message | Show original | Remove | Report Abuse
We are running Keri Doors 4.3 and are having trouble with the Attendance Detail reporting. Our configuration utilizes a controller for two access readers on two different doors. One of the readers are coded Reader Type - In, and the other is coded as Reader Type - Out. The report picks up reads from one of the doors on occasion; however, in most cases the program doesn't record any access at all on either of the doors--both in or out.
Can the problem be the result of an incorrect setting in the software, or is it in the hardware? Could it be a faulty board? Or perhaps it might be the result of a faulty Controller?
Any other ideas and/or solutions would be extremely helpful.
Sincerely,
Rafi Hecht Dynamic Diamond
Reply
- Rafi Hecht Aug 31, 9:35 am show options
Newsgroups: alt.security.alarms From: "Rafi Hecht" - Find messages by this author Date: 31 Aug 2005 06:35:07 -0700 Local: Wed, Aug 31 2005 9:35 am Subject: Keri Doors 4.3 Reply | Reply to Author | Forward | Print | Individual Message | Show original | Remove | Report Abuse
We are running Keri Doors 4.3 and are having trouble with the Attendance Detail reporting. Our configuration utilizes a controller for two access readers on two different doors. One of the readers are coded Reader Type - In, and the other is coded as Reader Type - Out. The report picks up reads from one of the doors on occasion; however, in most cases the program doesn't record any access at all on either of the doors--both in or out.
Can the problem be the result of an incorrect setting in the software, or is it in the hardware? Could it be a faulty board? Or perhaps it might be the result of a faulty Controller?
Any other ideas and/or solutions would be extremely helpful.
Sincerely,
Rafi Hecht Dynamic Diamond
Reply
- James Aug 31, 10:40 pm show options
Newsgroups: alt.security.alarms From: "James" - Find messages by this author
Date: Wed, 31 Aug 2005 20:40:28 -0600 Local: Wed, Aug 31 2005 10:40 pm Subject: Re: Keri Doors 4.3 Reply | Reply to Author | Forward | Print | Individual Message | Show original | Report Abuse
The setup with the readers sounds like it is intended for 1 door that has a reader to get in on one side and to get back out on the other side. If you have 2 seperate doors you shouldnt have an out reader configured. Before you can run a report you need to do a "Collect" from the system monitor
screen. Then when you run a report it will show all the new events.
James
- Hide quoted text -
- Show quoted text -
Reply
- Rafi Hecht Sep 1, 3:22 pm show options
Newsgroups: alt.security.alarms From: "Rafi Hecht" - Find messages by this author Date: 1 Sep 2005 12:22:04 -0700 Local: Thurs, Sep 1 2005 3:22 pm Subject: Re: Keri Doors 4.3 Reply | Reply to Author | Forward | Print | Individual Message | Show original | Remove | Report Abuse
In our setup, we have a two-door trap system. After entering the first
door, THAT DOOR must first close before one can go through the second door. Although both sides of each door are controlled by the same reader, one of the doors is Reader Type In and the other is Reader Type
Out. However, as I indicated, NEITHER of the doors are recording by our system. Yet, other unrelated doors, are being read, and reported correctly. Any suggestions would be highly appreciated.
Sincerely, Rafi Hecht Dynamic Diamond Corp.