DSC Power 832 - PC5501Z Keypad - Zone 1 Question

Check your programming to see if you have zone one assigned to the keypad.

Reply to
Tommy
Loading thread data ...

I've read the manual and have a question. Is the wiring for zone 1 different than the other zones? All of my other zones work fine except for zone 1. I know the contact is good and I have even replaced it on the panel with a jumper between ZN1 and COM and yet the system still sees zone 1 as open. Any suggestions?

-Russ

Reply to
Surebet

A jumper or a Resistor? Zone 1 works the same as the other zones. Try putting the resistor across zone one but make sure to disconnect the actual zone wires from it. This should narrow it down.

James

Reply to
J Barnes

Zone programmed for NO EOLR maybe?

Reply to
Bob La Londe

Figured it out. Actually it was because the keypad was setup to be used as a zone as well. I'm learning a great deal in this process and the people and messages in this group are helping. Thanks everyone!

Reply to