Re: 3 Phase Power

Apropos the earlier discussion in the 25Hz thread, I think both the US

> and Europe distribute three phase wye connected power. If you look at a > distribution pole, at least before the phases are split out, you will > see three well insulated wires, and a fourth wire that is earthed at > each pole. > I believe both systems provide single phase house current by attaching > a transformer from one phase to neutral/earth. If you go down a street > with three phase distribution you will see the transformers (pole pigs) > attached to each phase in sequence. When you get near the end of a > run, it may drop down to two, or even a single phase. If you are going > down a street with streetlights, there will likely be a line below the > main distribution lines carrying lower voltage for them.

I studied power a bit 30 years ago in but now my knowledge is a bit more limited so excuse any technical mistakes. Here in Raleigh, NC and I'm assume other CP&L/Progress Energy locations, they have been on a campaign for a while to loop all the 3 phase feeds from the substations so there are few if any "ends of runs". I don't know if this started due to Hugo & Fran, just happened at the same time, or was accelerated due to them. But it sure makes it faster to bring folks back "on the grid". Plus as a rule they don't tap transformers for houses directly off the 3 phase wires. They have runs of a one to a few blocks attached to a feeder drop below the 3 phase lines which helps keep the main lines running even when local problems arise. These feeders are connected with fuses to one of the 3 phase legs.

I learned most of this talking to a repair supervisor as it turns out my pole is one of the first visited after a major storm. It has the first disconnect switch for the 3 phase loop out of the substation. And I'm on the substation side. Plus my transformer is still connected directly to a 3 phase leg which means that I'm one of about 5 houses in my area to get power before anyone else within about 1/2 mile or so. I was told unless they had to change out the transformer they'd leave it connected that way.

When you come to a customer requiring three phase power, there will be three > pole pigs, one off each leg. I think in Europe these are also wye > connected, but some in the US are delta connected. Some places the power > company, at least in the past, got cheap and used two pole pigs to deliver > an "open delta" where the third phase is imputed. On a warm spring day > with the sun shining and the birds singing, this works fine. When the > loads get out of balance, all sorts of evil ensues. > There is, however, a reason for both wye and delta connections. Non > linear loads, and ever more are with the prevalence of switching power > supplies, generating harmonics. Multiples of the third harmonic, > called triplen (from triple n) currents add in phase on the neutral. A > wye-delta transformation traps them and keeps them out of the upstream > system, where large currents on the neutral can wreak havoc.
Reply to
DLR
Loading thread data ...

Cabling-Design.com Forums website is not affiliated with any of the manufacturers or service providers discussed here. All logos and trade names are the property of their respective owners.