Multiple T1 transmissions on Cat5E

My question is regarding the transmission of multiple T1 signals on Category-5E cables bundled together. The reason I have this question is one of my data center customers decided to extend (48) T1 lines from the Telco room to IVR equipment over (48) Cat5E cables. Then terminate on standard 48-port RJ-45 patch panel. The intent is to run each T1 on an individual Cat5E cable (ie. Tx & Rx within each cable). My cusomter claims that there would be no intereference between all these T1 lines running together in the cable tray. The distance is over 100 feet.

Normally, the way I design T1 cable runs is to either use 56-pair ABAM and terminate on a DSX panel; or substitute the ABAM with Category-3 and terminate each Cat-3 bundle one for Tx and one for Rx.

I was taught by an SBC engineer once that running more than 6-7 T1s in individual Category-5E/6 cables next to each other will cause interference or cross-talk. Is this true from your knowledge and experience??

Reply to
Tech Geek
Loading thread data ...

I've only run DS1s (up to 28) in separate transmit and receive cables, except when using individually shielded pairs. However, if the customer insists, get it in writing.

BTW, what are the customer's engineering credentials, that make him such an expert?

Reply to
James Knott

There is a difference between designing a cable solution for a

specific installation where you know what you are dealing with, and

designing a solution that will always work. (proper Engineering

design)

One of the most critical parameters in what you can "get away with" in

designing cable for T1 transport is the difference in signal level

between the various T1s. A T1 signal is reduced in strength as it

passes through the cable. At its generation, it is typically 6 Volts

peak to peak. This is called 0dbDSX0 (commonly refered to as 0db or

dsx0). It is the reference level used at DSX cross connect points.

In a CO, at a T1 DSX, there can be literally 1000s of T1s running

through cross connect trays unshielded. This only works because they

are all at the same signal level. There is no significant Near End

Cross Talk (NEXT) generated.

This "same level" phenomenon is why you can bundle multiple transmit

signals or multiple receive signals into a common Unshielded Twisted

Pair (UTP - ie: Cat5) cable or in a shelded bundle of a T-Screened

cable (group shielded bundles in a common cable) without worrying

about NEXT.

However, it is not uncommon for received signals on a normal

(repeatered) T1 line to be significantly below the level they were

transmitted at. (T1 signal degrades at a rate of 4db to 6db per 1000

cable ft depending on wire gauge and splices, etc) At the telco

demark (point of hand off of a T1 line at a customer's location) the

signal will be between dsx0 and -16 db DSX0 by engineering standard.

(-16 db is 16 db below the nominal transmit level and is approximately

1V ptp)

Another place where 0dbDSX0 signals are common is if the telco

delivers the T1 by DSL or M13 multiplexer (fiber optics). These

devices output at or near dsx0 level and if your T1 is delivered by

one of these methods, the signals will be at full strength at the

demark.

Generally, if the signal levels are within 7.5 db of one another

through out a cable length, NEXT is not significant, and you can "get

away with" running UTP for T1. However, if a receive signal at -10 db

and a transmit signal at 0 db are run through a UTP for even

relatively short distances, you can expect to get enough cross talk

to cause bipolar violations (errors). This is especially true if

multiple T1s are run through the same bundle. The lower strength

signals will all be corrupted.

In summary, if you know that the signals are at the same levels and

your distances are not too long (less than 500 ft) you can use UTP

and not worrry about Cross Talk. Just be sure to physically separate

UTP cables carrying signals of different levels.

However, if you know that the signals are not the same level, or you

don't know what the signal levels are or how the T1 lines are

engineered, you can design a solution that will always work. This is

why the telco standards for wiring were developed. They don't know

what they will run into at each installation because they have T1s

coming into an office and cannot always plan for the characteritics

of each one. By using individually shielded twisted pair wire, or

T-Screened cable with all of the transmit signals at the same level

in one bundle and the receive signals at the same level in a separate

bundle NEXT can be avoided.

Otherwise you are left with "sometimes it works...."