Lightning has damaged the "initiating" relay of four 2112/24ATR's. Each of the four units exhibit the normal pulsing red LED. Each also sounds its internal horn when the test "button" is depressed. However, each of the four do not place a short across the signalling circuit, thus the panel and all the other detectors do not know that any of the four has tripped. When I "short" the terminals behind the detector the panel and other smoke detectors leap into action and do their temporal thing, plus sounding additional electronic sirens, in a temporal pattern, though not in unison with all the smoke detectors.
We monitor/service this house with twenty-one SD's. The "aux" relay of the 2112/24ATR is used to light up two panels, each with five red LED's indicating which area of the house the smoke is in. Installed in 2001.
The conclusion is that the "initiating" relay that places the "short" across the pair is not being energized, or the points are frozen open.
I replaced each of the four units temporarilly with 2112/24AT's (which do not contain the "aux" relay). All the other units were successfully tested today (fire department present and signed off on Certificate of Compliance - house being sold).
Anyone have any of these System Sensor units in their original boxes that I can buy?
The recommended replacement is 4WTAR-B, but I'm not sure that the reversing relay (RR-2) in the present system will act on the 4WTAR-B in the same fashion as the reversing relay (RRS-MOD) specified for use with a group of 4WTAR-B's.
The RR-2 and the RSS-MOD act differently on the power circuit. The RR-2 simply reverses the polarity, and then opens/closes its relay to produce the temporal pattern, in unison, in all the detectors. The RSS-MOD operates in a different manner (don't know how) on the
4WTAR-B's to produce the temporal pattern, all detectors in unison.One unfortunate conclusion that I have reached is that the pulsing red LED is an indicator that, as a minimum, there is power at the unit, and that the "initiating" relay is NOT supervised within the detector. Here I have four non-functioning relays, and no outward indication that they are damaged, and incapable of triggering an alarm elsewhere on the premises or at the central station.
Another good reason for periodic testing of smoke detectors, especially after lightning storms!
Thanks. Charlie