Re: Electrical Grounding

What is the effect of having an electrical ground
> close to a telecom (telephone land line) ground and
> what is the recommended distance they should be apart.
The "recommended distance they should be apart" is zero: both grounds
should be bonded together at a common ground point.
In the United States, the National Electrical Code specifies that ALL
electrical systems entering a building must be bonded together and
grounded to an approved grounding conductor at the point of entry.
This includes:
- Electrical power neutral conductor
- Exterior electrical circuits for lighting, water pumps, etc.
- Telephone lightning protector
- Telephone shield and/or messenger, if any
- Cable TV shield
- External antennas (amateur radio, radio, TV, DBS, etc.)
It also includes fire and police alarm wiring systems if any. It
might be a bit embarrassing if a fire alarm system started a fire.
There's an excellent article about all this at
formatting link

Neal McLain
Reply to
Neal McLain