Re: Electrical Grounding

Nov 17, 2006 0 Replies


What is the effect of having an electrical ground


> close to a telecom (telephone land line) ground and
> what is the recommended distance they should be apart.

The "recommended distance they should be apart" is zero: both grounds should be bonded together at a common ground point.


In the United States, the National Electrical Code specifies that ALL electrical systems entering a building must be bonded together and grounded to an approved grounding conductor at the point of entry. This includes:


- Electrical power neutral conductor - Exterior electrical circuits for lighting, water pumps, etc. - Telephone lightning protector - Telephone shield and/or messenger, if any - Cable TV shield - External antennas (amateur radio, radio, TV, DBS, etc.)


It also includes fire and police alarm wiring systems if any. It might be a bit embarrassing if a fire alarm system started a fire.


There's an excellent article about all this at

formatting link


Neal McLain