> It never ceases to amaze me that for every rule there seems to be a
> different opinion.
>
> TIA Les
> ============================================
>
> This is a question for Nick to help keep his brain functions working. >
> NFPA 72 says that the pull station should be mounted at 42-54" AFF >
> ADA says that the pull station should be mounted at 48" AFF
>
> PA Title 34 Part 1 says between 36" and 44" AFF
>
>
> So what does ICC ANSI A117.1-2003 say???
>
> I can't seem to find an exact reference to this listing.
>
> Nick can you quote the section on this item???
>
> Thanks in advance.
>
> Les
>
>
>
Mounting height for NFPA is 42" to 54", mounting height for ADA is 15" to 48" front reach and 52" for side reach, ANSI refers back to NFPA