Neutral wire at switches for outlets?

I know this is a stupid question, but is there any reason why switches for outlets can't have neutral wires? I'm currently building a house, and I requested a neutral wire at all the switches. The light switches do have neutrals, but the switched outlets don't. Most of those are in a box with a light switch, so there is neutral in the box, but a few aren't. Does each switch in a multiswitch box need a neutral coming in? Any help for this newbie would be appreciated. Thanks!

Ben

Reply to
Ben
Loading thread data ...

ANY switch can have a neutral but most don't need them as wired (for no automation). As long as you are paying for the work, you can insist on them so that you will have them available for future automation uses.

Reply to
B Fuhrmann

Ben,

The preferred method of wiring is to bring power (hot and neutral) into the switch box, interrupt the hot leg with a switch, then carry the power (hot and neutral) on to the load, be it switch or outlet.

Sometimes, though, it's quicker, easier, and saves a lot of Romex to run power to the load, then use a piece of romex to extend the hot into the switch box. The white wire then becomes a switched hot, and is marked with black tape or marker. This results in no neutral.

If they wired a box without a neutral even after you asked them to, it is their responsiblity to fix it. You need to get your GC on your side in terms of cost: the electricians almost certainly WILL try to bill you for their mistake!

Reply to
E. Lee Dickinson

I have a somewhat related question:

In my home, there is a 3-way circuit which controls a group of outlets and a group of lights. In the process of stripping the outlets out of the circuit, I discovered that the circuit hot comes from the breaker, but the neutral comes from another (unswitched) circuit of outlets.

By my thinking -- the neutrals are all common at the breaker anyway, so it shouldn't make a difference. Is there any reason for me to be concerned about this?

Reply to
E. Lee Dickinson

Yes, I second this notion. Best to bring the hot/neutral/ground to the wall plate and then run a four-wire (hot/neutral/switched/ground) to the ceiling or other switched fixture. That way if at some point in the future you install a fixture that needs it's own power you'll have it there already. Things like ceiling fans operated by remote often their own power full time, in addition to that controlled by a wall switch. Outside motion sensors also. But basically it's your house, get it the way you want it. Wire is cheap and the labor to do this is no different than any other method. Granted, it will require having 3 conductor romex in addition to the regular

2 conductor but that's a negligble difference.

-Bill Kearney

Reply to
wkearney99

Just specify to the electrician that you want a neutral at each switch and he can do it. I did that in my home and even if it wasn't used for anything else, I have a neutral tail available at every switch.

Reply to
brobin

Close, but one problem...

The white wire in these "switch leg" or "switch loop" circuits is the always hot wire and the white wire is the switched hot wire. This makes identification of a unknown white wire easier since it is always hot not just hot when the switch is on.

This is covered in 200-7(c) of the National Electrical Code where the "conductor with white or natural gray insulation or a marking of three continuous whit stripes is used to supply the switch." The requirement to remark the white wire with black came in the 1999 NEC.

Reply to
Lewis Gardner

Yes. There are a few cases where this is legal but it is a bad practice even then and can pose a safety risk.

The theory about them all being equal because they are connected at the breaker is only valid if there is no resistance in the wire or connections and all connections are 100% reliable.

If the neutral is connected to a 2nd circuit and ANYTHING is on (including night lights, or AV equipment that has a remote) they are putting a voltage on the neutral for that circuit. Depending on where your branch of the neutral is connected to the circuit, the voltage on it will vary but will not be 0.

Reply to
B Fuhrmann

I can't speak for the US regs, but that's not allowed in UK regs. Only the earth/ground wire is allowed to be cross-connected between different circuits. Cross-connecting a neutral like this could result in circuit which has been isolated for work to be carried out on it actually being live due to the cross-connect.

Reply to
Andrew Gabriel

Yes, you should be concerned, at least from my UK perspective. Here it's normal to disconnect one circuit to work on it, leaving the rest of the circuits live. If you disconnect one live and one neutral, your safety depends on that neutral *not* being connected to any other live though an appliance. So it's not permitted to mix the neutrals.

You said "the neutrals are all common anyway" and that is true normally, but not always.

Reply to
Mike Barnes

Can you try that again? You've confused me, now. :)

My way of thinking (in the US) is that an unknown white wire is going to be assumed neutral. An unknown black wire is going to be assumed hot. If I'm wrong, I'm wrong.. but I've always seen white with a black mark as the switched leg, black as the always hot leg.

Reply to
E. Lee Dickinson

Went to dinner, came back, re-read, and understood. Though I do believe you meant "black is switched." That way, there's no way to assume the white is neutral... it's always hot. If it were switched, and off, you might think it was neutral.

Got it. Thanks!

Reply to
E. Lee Dickinson

"E. Lee Dickinson" wrote in news:ddi7pn$jo3$ snipped-for-privacy@solaris.cc.vt.edu:

Answer: It depends.

I believe that this is permitted in the U.S.A. as long as:

1) The two circuits are on opposite phases of a split phase service. 2) The two circuit breakers have equal limits and are mechanically tied together so that tripping or turning off one breaker shuts off both.

Rule 1 is important because two circuits sharing a neutral on the same phase could potentially double the current in the wire. Being on opposite phases, the current is the difference between what the two circuits are using (leaving out reactive loads).

Rule 2 is important because it prevents shocks during servicing. Otherwise, with one circuit shut off, the other circuit can make the neutral hot through any lights or appliances that are left on. I have been shocked (*) by such a circuit that did not have tied breakers because it was wired before this rule was made part of the NEC.

(*) I was shaken and greatly surprised but learned a valuable lesson: Use a meter to verify prior to touching!

In the cases that I have seen, the wiring from the circuit breaker panel to the loads used Romex with four wires in this case: Ground (bare), Neutral (white), Line 1 (black), Line 2 (red).

Other countries may be different. Particular locations within the U.S.A. may be different. Older wiring may be different. Mistakes can cause differences.

Reply to
Ian Shef

While all the above is true, my experience with piped (conduit) wiring in residential new construction is that shared neutrals are the norm for 15 and

20 amp circuits, not the exception. Each pipe leaving the service panel will have several hot wires and at most two neutral wires, unless the associated breakers are ground or arc faults. In these cases the neutral wires are dedicated and usually slate/gray rather than white.
Reply to