Re: Causes of Ground Faults

I have been asked to present a training seminar regarding fire alarm

>systems, in particular addressable systems. I am looking for common >causes of Ground Fault Troubles that people have come across. Any one?

I'd say the most common is nicking, skinning, and burring the wire when it's being pulled. Common hang ups are un-reamed EMT connected to fittings (couplers etc.. ) , iron beams with sharp edges etc...

Pulling too hard or forcing the cable will often result in bad news such as stretching and breakage. Pull slack in multiple locations around obstacles, with help if possible, to reduce the urge to manhandle it.

Some installers still don't know how to strip the proper length of copper for device termination and leave too much hanging out to get grounded on the back box when the device is secured to it.

Even worse than not stripping the proper length of copper for landing on the terminal: is when guys strip the outer layer of a cable jacket (plenum is the easiest to muss-up) with their strippers and use that first cut.... Why do you think the cat's hair is in there??? Use the cat hair!! Pull the cat hair down the length of the outer jacket and cut away the original jacket strip... so there is no chance of nicks, opens, or shorts.. sheeze~!!! Use the damn cat hair...

On addressable sytems using isolation modules is a huge deal too.. explain them.

Reply to
G. Morgan
Loading thread data ...

Morgan you got the prize,, number one problems we've had in 24 years on install "contract electricans for emt install" they do all your listed faults and they also do the crawfish too.. LOL RTS

Reply to
Rocky T Squirrel

Heh.. I wish I could blame the electricians for all my grounds! I learned at the School of Hard Knocks! I wasn't always so careful. But that's what experience is, something you can't get from a manual.

Reply to
G. Morgan

If the electricians are that bad, why not just do your own EMT? js

Reply to
alarman

Because on large new construction jobs the electrician usually bid the job and you're his sub, and he is the sub for the general contractor. The electrician usually wants to run all the thin wall because he is doing it all the rest anyway. It is good for the fire alarm installer because if the electrician does it, and then if there is a problem with the pipe, it's always his problem. It's okay to run a stick or two yourself, but who wants to run all the emt anyway?

Reply to
Roland

Not me, I suck at it.

Reply to
G. Morgan