DC power question

Can anyone tell me where the [best/proper/only/traditional/whatever] location to tie the battery return line on a DC powerplant to ground is? It's the + lead on a -48v supply. I know for AC that nuetral is tied to ground only at the service entrance and noplace else. I can't seem to find the DC equivalent of that documented anywhere.

I'm duplicating a CO on a very miniature scale for a test lab. 4 racks, 1 rectifier, 1 battery string, 2 fuse panels - one pretending to be the main DC switchboard.

OTOH, have you seen the new (new to me, old fart that I am) grounding standards? WOW! They documented them to death... except for the battery return :-(

Reply to
Bill H
Loading thread data ...

Let me add a little bit to clarify that excellent description.

Every piece of equipment should have three separate connections.

-48V, +48V, and Ground. The +/-48V are as described.

The ground should have a single common point for the entire building (or more specifically, for each part of a building that has a unique AC power distribution system). Each floor should have a single common point (all of which are individually connected to the building's common point).

Each row of equipment racks should have an individual connection to the floor's common point. Typically that is done at the top of the racks, and each will have a copper bus bar at the top, and each bus bar is connected to the adjacent rack's bus bar.

Each rack then has, on each side, a ground wire extending from top to bottom.

Each piece of equipment is connected to one or the other of those ground wires. Just as the racks are connected to a common ground bus across the top, sometimes a number of similar equipment chassis are strapped to ground by a common strap that goes from one chassis to the next and ends up connecting to all of the chassis and to ground, exactly once per item.

The exact voltage depends on the type of battery, and that value should be obtained from the manufacturer's specifications.

To end with, let me pull out one sentence from wdg's description, and emphasize it even more:

"The *ONLY* connection between +48 return and GROUND should be at the distribution panel in the power room."

The positive side of the battery and the building ground system connect exactly one time only.

Reply to
Floyd L. Davidson

Battery return (unswitched/unfused +48) is bonded to frame/building ground (which should be one & the same) at the main distribution panel (only) where the batteries and rectifiers come together.

I cannot quote the precise spec, but there should be an infinitesimally tiny and insignificant amount of measurable current in the frame/building GROUND leg.

Equipment load requires two wires (- 48 supply and return) all the way back to the dist panel. Equipment should also be bonded between it's frame/chassis and the nearest ground. As above, there should be no current in the ground lead. Equipment bonding (ground) lead should -NOT!- be connected to the +48 return lead at the equipment end. The ONLY connection between +48 return and GROUND should be at the distribution panel in the power room.

Measured at the source, with rectifiers/chargers >Can anyone tell me where the [best/proper/only/traditional/whatever]

Reply to
wdg

That's exactly what I was looking for (and what I thought it was).

Thank you both for confirming it.

-- Bill H. [my "reply to" address is real]