Need Programming assistance on a Notifier SFP-1024 Control

Have a question or want to start a discussion? Post it! No Registration Necessary.  Now with pictures!

Threaded View
I am receiving 2 daily test signals from the above panel.  Notifier  
refuses to provide programming assistance, and the manual does not make  
it clear re: double reporting.  Silent Knight used to have a Must call  
option, which caused multiple signals, but I figured that out in the 80s.

tia,

John

Re: Need Programming assistance on a Notifier SFP-1024 Control
Quoted text here. Click to load it


Some FACP manufacturers have their panels setup so that they can *only* send  
TWO test signals when monitored.  One on each line.  I don't know much about  
Notifier, but they may be that way.  I have a couple of them on Sole Path  
Cellular and the extra air time is annoying, but I do make money on them.  I  
have alarms dialing my own toll free lines, so extra call time is only a few  
cents per signal on those that are on landlines.  


Re: Need Programming assistance on a Notifier SFP-1024 Control
On 07/03/2014 10:20 AM, Bob La Londe wrote:
Quoted text here. Click to load it

This system is in our LATA so I have it dial into a local phone line.  
My concern is the dispatchers having to deal with 2 phone calls every  
night.  This is the only one that does this.  No reference is made in  
the manual to sending 2 signals every day.  Gee, wait for the next nfpa  
72, we'll be getting 4 signals per day, one every 6 hours!

John


Re: Need Programming assistance on a Notifier SFP-1024 Control

On 07/03/2014 10:20 AM, Bob La Londe wrote:
Quoted text here. Click to load it




John  try matching the Notifier panel with a Firelite  panel  ( their made  
in the same factory by the same company)

then  call Firelite with your problem  using the Firelite panel as  
reference..

My experience has been the panels are the same just the names and part  
numbers are different..

RTS



---
This email is free from viruses and malware because avast! Antivirus protection is active.
http://www.avast.com


Re: Need Programming assistance on a Notifier SFP-1024 Control
On 07/04/2014 07:10 AM, RTS wrote:
Quoted text here. Click to load it
love it, an outside the box thinker!

john


Re: Need Programming assistance on a Notifier SFP-1024 Control
Quoted text here. Click to load it

Interesting, I think it was a Firelite panel I first noted what you  
described.  Dual daily test (one on each line) and no apparent way to change  
that.


  


Re: Need Programming assistance on a Notifier SFP-1024 Control

Quoted text here. Click to load it



your listed  Notifier SFP-1024   seem to be the same as a Firelite  MS-5-10  
(5 zone or 10 zone)

the DACT  programing   "Report Style"  can select     1=backup only,  
2=both,   3=first available

also in the DACT programing   "Test Time Interval"    1=24 hours,    2=12  
hours,  3=8 hours  (page 2)   1=6 hours

That might be the place you need to look for changing the dial out...

RTS


---
This email is free from viruses and malware because avast! Antivirus protection is active.
http://www.avast.com


Re: Need Programming assistance on a Notifier SFP-1024 Control
On 07/06/2014 05:36 PM, RTS wrote:
Quoted text here. Click to load it
Sorry about the delay to respond.  I am working my email off 2  
computers.  I did find the Firelite MS-5510 ? Its on the computer at the  
office.  The backup is not the answer, as I would be receiving double  
reporting on the alarms during inspections.  I found an entry to send  
the daily test to the second phone number.  I am going to turn that off  
the next time we are there.  If this is still on the ng, I will respind  
with the results.  The biggie is the notifier to Firelite link.

thanks,

john