Posted by on November 12, 2007, 8:15 pm
Please log in for more thread options wrote:
> N9WOS wrote:
>
> > >I am planning to install some new solar panels on a steep mountain slope.
> > >The line will have to run about 250 to 300 linear feet to get to my house,
> > >inverter, batteries, etc.
>
> > > Is this feasible? How do I figure what type/size of line I will need for
> > > this (and the approximate cost)?
>
> > (cross posted to all news groups that I found the question in.)
>
> Thank you for that.
>
> To summarise, the length of the cable run may be practical but you need to take
> into account the current, operational voltage, acceptable voltage loss in the
> cable etc.
>
> There is no one simple answer. It has to be CALCULATED for every installation
> where cable length is a concern.
>
> Graham
Well there is one simple answer. The higher the voltage, the lower
the losses. The fatter the cable, the lower the losses.
You need to know that the loss is equal to the current squared times
the resistance.
P = I^2 * R
All copper wires come with specification values for resistance in ohms
per linear meter (which is directly proportial to the inverse of the
cross-sectional area of the conductor. )
Say you have a 1000 watt array at 200 volts. At full sun, you would
expect it to produce a current of 5 amperes.
Therefore if your cable run has a resistance of 2 ohms, then the loss
would be 25 * 2 = 50 watts.
|