Strange X10 Lamp module problem

Here a new one on me. I have used X10 in my house since it came out and have never seen this. I have 2 lamp modules plugged into the same outlet strip. One is a stock lamp module, the other is a lamp module, but with the solid state relay modification found on a few on-line sites. It has worked perfectly for some time. So this modification actually makes it a silent appliance module. But, it's still a lamp module at heart, only the output is a little different. The are both set to B1. The SSR modified module has 2 lamps (w/CFLs) connected to it, hence the SSR. The other one has a heated warming blanket. Last night, both were on and all of a sudden, both just shut down by themselves ... this is not the strange part. After, neither would respond to any X10 commands. I only used a wireless remote with transceiver for testing. I probably should have tried a direct X10 command from a manual controller, but I don't think that would have made a difference. And I never touched the transceiver, only the wireless remote. At first I blamed the modification, as I hadn't noticed that the unmodified module was also off, But then I discovered it too was off and wouldn't respond either. After powering down bother modules and re-powering, they now both work perfectly! I haven't a clue as to what could have caused this problem. It had to be some "command" or pseudo command (noise?). There are only 2 houses on the outside transformer. And, we are pretty far from any neighbors making it difficult to get rogue RF transmissions, i.e. lots in the subdivision are 3 - 4 acres. And the one neighbor on the same transformer doesn't have or even know what X10 is. Any ideas??

Reply to
Art Todesco
Loading thread data ...

There have been many reports of sudden plagues of random ONs and/or OFFs after the installation of a "Smart" Meter by various electrical utilities in various parts of the country. All of them appear to use LonTalk (although identifying it by the ANSI standard number) to communicate between meters and the Data Aggregator which usually serves all of the meters on the same transformer. It appears to affect X10-made modules and switches (but not those made by Smarthome).

Reply to
dlh

We have an RF reading electric meter in this house. The guy from the power company parks up at the top of the mountain and can access everyone below. But this problem occurred at night and the modules both appeared to lock up in the off condition, until they were power cycled. If it were only one, ok, but 2, side by side, on the same house and unit code? And, there were not other lockups in the entire house. Weird.

Reply to
Art Todesco

Per dlh:

Just to make sure: would it affect hard-wired X10 modules?

I've been beating my brains out for the better part of a year trying to figure out why one of my modules (located in a relatively inaccessible place) keeps getting turned on.

Until now, I've been thinking either defective module or some neighbor using X10's on the same-lettered scheme.

Reply to
(PeteCresswell)

I don't recall anyone reporting problems with hard-wired modules specifically but I suspect they are as vulnerable as the others.

Reply to
dlh

Who is your electric utility? Duke Energy seems to have the most problems and it's not only when the meter is being read.

Reply to
dlh

It's definitely Duke. The power is not very constant. I even see voltage drops from heat pump motors starting that are not in my house .... most likely, the guy across the street on the same transformer. But, X10 had been really clean. Much cleaner than in my old house in suburban Chicago (for X10, that is). I have called Duke for voltages going high, like 125 -130 volts. When I called them, they immediately said it was their problem and corrected it within an hour or so. But, over the months, it has crept up again, to about 120, which I guess is ok. I think it crept up because others on the same feed complained about low voltage and they corrected it the easy way. BTW, at 123 volts or so, I've had some electronic equipment get squirrelly. That's what made me start looking at voltages.

Reply to
Art Todesco

  1. The Noise could be code dependant.. switching to different module/house code.
  2. I have found that certain motion activated or dusk/dawn light (inside or outside) control units often generate lots of RF line noise.. Ergo the problem shows up at after dusk.
  3. Any of the cheaply made non-fcc approved, ac to dc walwarts could make lot's of RF noise.. (Start up-plugging things, or flipping breakers.)
Reply to
T. Keating

Duke and other utilities are using an Echelon Data Concentrator (or similar devices made by others but still using LonTalk). I think there is one per transformer and they act as a router with the ability to query the meters, shed loads, etc. and send usage data to the central office over the powerlines. They may not have implemented all of the features initially. In the Cincinnati area numerous X10 users have seen random turn-ons which appear to be caused by very high amplitude

86kHz signals from the data concentrators. Duke has told one person that Echelon is working on a filter that they will try at his residence when received.

formatting link
Jeff Volp has found a combination of clamp-on ferrites plus a filter across the two hot legs that also seems to filter the signals.

I suspect it's the amplitude (which rises in response to "noise") of the signals that is causing the problem, acting like spikes which X10 has acknowledged causes similar issues. In two cases, people experiencing the problem found that Smarthome made X-10 modules set to the same address appeared to be immune. This was, however, a very small sample size so YMMV.

This may or may not be the cause of your issue but I think it's worthwhile for all X10 users to be aware of it with the nationwide rollout of smart meters.

I live across the river from Cincinnati and my area was an early test area for Duke about 5 years ago. I saw no X-10 issues (most of my gear is not X10-made) but did have some inexpensive appliances with electronic controls go berserk.

Reply to
dlh

Well, this was a random turn off, but once it was off, it was locked and could not be turned back on, until I power cycled the modules. And, in my area, Duke uses an RF system to read the meters. I talked to the Duke guy, whose son lives in my subdivision, and he said that he goes to the highest point and reads all the meters below, from his truck. He actually changed out my meter because it was not the proper type that could be read from his RF reader. Also, this happened at night, maybe

10PM, when I seriously doubt that he was doing any meter reads.
Reply to
Art Todesco

When a lamp gets turned off the impedance of the house circuit increases and the noise can be higher at the unit than if the circuit had more load on it. Standing waves and reflections can increase the amplitude of the noise when unloaded.

I always had problems with my wireless X10 units. They would think they heard signals and repeat them. Usually all lights on signals would happen or they would lock up and send continuous noise locking up the system.

Many smart meter systems send signals regularly and intermittently to the other smart meters so that the master data gatherer can access meters "hidden" from where it sits. Number of data jumps can be limited in the meter software as that can also lock up the network by perpetual repeats of data bouncing around.

10PM, when I seriously doubt that he was doing any meter reads.
Reply to
Josepi

What's plugged into it?

-- Bobby G.

Reply to
Robert Green