I have and use a SH 1132CU with the "plus" software.  Basically, my
house is on house code B, however, some stuff is on C.  I have front
floods on C10 and rear floods on C9.  In the 1132 programming I have a
macro that basically says, if B8 goes on, then do a C9 on and a C10 on.
  Similarly, there is a 2nd macro that says, if B8 goes off, then do a
C9 off and a C10 off.  However, if one of the manual controllers, set to
house code B, does an "all off", the 1132CU doesn't do anything.  I was
wondering if someone has found a way to program the 1132CU that would
basically say, if you do a B, all off, it would recognize that and
subsequently do a C9 off and a C10 off.  The reason for putting the
floods on C9 and C10, was to free up B9 and B10 for other things.  Any
ideas?  Thanks.

Re: Question about SmartHome 1132CU programming
Quoted text here. Click to load it

There is a set up on the 1132cu plus for the letter all on or letter
all off
set it up as
If B all Off Turn C8 off
Delay 3 second
turn c9 off


Re: Question about SmartHome 1132CU programming
On 4/28/2012 11:14 PM, Harold Sharpe wrote:
Quoted text here. Click to load it
Thanks, I did it and it works.  I never looking in the drop downs where
it appears, so I never found it.  A 'B All Off', now also does a 'C All
Off. '