I currently have a Napco Gemini P816 panel serving as my alarm panel.
I also have a GEM-X10 module (which I haven't installed yet) and an
always-on PC providing home automation functions. The PC will
communicate X10 and Insteon (light fixtures) using a PLC right now,
but will eventually support whole-house audio, phone line integration
(including voice commands), HVAC tie-in, etc.

All of my doors and windows are wired up to the P816 panel, which,
from what I understand supports the GEM-X10 module but does a very
poor job of it. The GEM-X10 module seems to appear to the panel as a
group of relays, which I believe I can only "trigger" (e.g. send an
X10 command to my PC) on EVENT changes. I've viewed the event log
(through the serial adaptor add-on and QuickLoader software) and I
only see alarm status changes (e.g, Alarm Armed, Alarm Disarmed, Alarm
Activated or Deactivated). I don't see any "events" for zone status
changes, such as when the front door is opened.

My intent is to be able to monitor each zone to send a command to the
PC to make an intelligent HA decision on what to do with it. For
example, when the front door is opened, send an insteon command to
turn on all the lights on the first floor. Or when a window is opened,
turn off the AC unit. Or when the alarm is triggered, blink all the
lights in the house (successive commands of "instant on", "instant
off").

I believe there are a few ways I can fix this situation, assuming the
P816 does not have the capabilities to do what I am trying to do:

1) Replace the panel with a P3200, P9600, or Elk M1G or some other
type of panel. Would I need more than a P3200 to do what I am trying
to do? I realize a panel like the Elk M1G can automate a lot of the
current functions I am planning to do with the PC, but I don't mind
having the always-on PC. I believe this would give me more options and
capabilities as long as I don't mind having the PC running 24/7/365.

If I did decide to change the panel, is it fairly straightforward?
Could I simply "download" the configuration from the P816 through the
Quickloader software and "upload" it to the P3200? I have the dealer
code, but I'm not sure if configurations can be easily "ported" like
this from one model to another.

2) Another option might be to somehow split (y-out) the door and
windows contact terminals before they get to the P816 panel into a
device such as the Smarthome EZIO 4 Input/2 Output Relay Controller
(http://www.smarthome.com/31274.html). I'm not sure if this would do
exactly what I am trying to do though, since I'm not that familiar
with the product. Also, I don't know if I would need any additional
resistors or if it's even possible to split the contacts into this
second device (either in parallel or serial). Assuming I could split
the contacts, are there any other devices that can send X10/Insteon or
some other HA-software-compatible commands by contact status changes?

Any help or suggestions you can provide are greatly appreciated!
Ken


Posted by on September 26, 2007, 12:08 pm
Please log in for more thread options
OK - Update. I decided against trying to split the contacts. I think
I'm just going to upgrade to the Napco Gemini P3200 panel.

Does anyone know if I can have individual X-10 commands sent for each
zone-trigger? For example, send an X10 command when the dining room
window is opened (assuming the alarm is not set)? Would this be the
"relay follows zone" function described in the manual?

The manual description is as follows:

Relay Control (External Relays)
In addition to the three relays provided on the motherboard, up to 24
external relays (8 per RB3008 Relay Module) or X-10 devices (24 per
GEM-X10 module) may be controlled from the keypad, by event or by
schedule through the use of PCD3000 downloading software. Program
these outputs to activate by event on PCD3000 External Relay Control
screen, or by schedule on the Event Scheduler screen.

Relay Follows Zone
External Relays can be programmed to follow an open or shorted zone.
On the PCD3000 External Relay Control screen, program the External
Relay to .follow . an open zone, or to .follow. a shorted zone.

Relay / X-10 Mapping
It is possible to have a relay or X-10 device activate for multiple
events, with a maximum of 24 events. This allows the relay or X-10
device to be activated by multiple events or conditions. This is
programmed by assigning or mapping events to relay numbers. PCD3000
must be used to program Relay/X-10 mapping. Referring to the PCD3000
External Relay Control screen, the .Relay / Entry#. column typically
indicates the number of the relay which will accept the commands on
that line. However, the .Map. column, which is used to transfer the
function defined on that line to a device on another line.


Posted by Robert L Bass on September 26, 2007, 6:19 pm
Please log in for more thread options
>
> OK - Update. I decided against trying to split the contacts. I
> think I'm just going to upgrade to the Napco Gemini P3200 panel.
>
> Does anyone know if I can have individual X-10 commands sent for
> each zone-trigger?

Yes, you can. The P9600 can send X10 commands and/or trigger
programmable relays for each zone event, area events, system events,
user actions and scheduled events. The schedules can be as simple as
"5:15 each day" or as complex as "7:45 pm on the third Thursday of
each month".

BTW, in addition to scheduling rerlays and X10 commands, the P9600
can schedule auto-arm in case the client forgets to arm his system.
It will do much more advanced stuff as well if you want to fool
around with the software.

> For example, send an X10 command when the dining room window is
> opened (assuming the alarm is not set)? Would this be the "relay
> follows zone" function described in the manual?

Yes, except that if the X10 (relay) is set to "Follow Zone Open" it
will do so regardless if the system is armed.

> Relay / X-10 Mapping. It is possible to have a relay or X-10 device
> activate for multiple events...

Yes. You have 96 "code lines" available. Each line can trigger one
relay (X10 output) from a single event. By repeating either a relay
number or an event type in multiple lines you can control more than
one relay per event or control one relay from multiple events.

I've used these features with the Napco P9600 extensively over the
years. Systems would arm and disarm on schedule, bypass specific
zones and even power down motion and glass break detectors on
schedule. This was done to accommodate the needs of Orthodox Jewish
clients whose religious observance prohibits them from operating
electronic equipment during certain holy days, as well as on the
Sabboth (sunset Friday until sunset Saturday).

I designed one system using the P9600 to allow one-way motion in a
stairway at night. If someone got up at night and wanted to descend
the stairs to reach the kitchen the system would bypass motion
detectors until they returned. However, if someone tried to ascend
the stairs while the system was armed for the night the alarm would
go off immediately.

Another dealer I know used X10 to control a light in the window so
that the client could see that the system was armed before they drove
away.

> with a maximum of 24 events...

On the P9600 you have up to 96 events. That does not include
time-scheduled actions. You can create up to 255 scheduled events to
control lights in a pseudo-random pattern, heat up the Jaccuzzi at
6:15 each Friday, electronically lock the doors after the exit delay
expires or just about anything else you might think of.

> This allows the relay or X-10 device to be activated by multiple
> events or conditions. This is programmed by assigning or mapping
> events to relay numbers. PCD3000 must be used to program Relay/X-10
> mapping...

The new software is called "Quickloadr for Windows" (that's not a
typo; Napco dropped the "e"). You can download the software from my
website if you like. It's free. You'll need the Napco PCI-MINI or
PCI-MINI-USB to connect your laptop or PC to the panel.

If you need help programming the P9600 give me a call. I'll be glad
to walk you through it. Most of the stuff is easy but there are a
few items that might not be intuitive to a newbie or DIYer.

--

Regards,
Robert L Bass

=============================>
Bass Home Electronics
941-925-8650
4883 Fallcrest Circle
Sarasota · Florida · 34233
http://www.bassburglaralarms.com
=============================>


Posted by Frank Olson on September 26, 2007, 9:05 pm
Please log in for more thread options
Robert L Bass wrote:
>>
>> OK - Update. I decided against trying to split the contacts. I think
>> I'm just going to upgrade to the Napco Gemini P3200 panel.
>>
>> Does anyone know if I can have individual X-10 commands sent for each
>> zone-trigger?
>
> Yes, you can. The P9600 can send ...


<snip> Read the OP's response before you "jump in" with information on
a panel he isn't even installing... Sheesh... What a maroon!

Posted by on September 26, 2007, 9:14 pm
Please log in for more thread options
Thanks Robert.

Do you know if your statements apply to the P3200 panel as well? It's
about 25% of the price of the 9600 panel, so if it can accomplish my
requirements, I'd rather spend the extra money on light switches. :)

Also, do you know if the Quickloadr software will allow me to upload
the config from my P816 to my PC and then simply download it to the
P3200 (or P9600)? Does the Quickloadr software take care of any
conversion necessary? The reason I ask is because I have my P816
monitored by an alarm company that configured and supports the P816.
If I can port all of the settings over to the P3200 without their
support, I don't see why they would have a problem with me changing
the panel.

Thanks,
Ken


Similar ThreadsPosted
Napco Panel, X10 Use, HA Software - HELP! September 26, 2007, 9:54 am
Advice on Patch Panel to Patch Panel Config January 17, 2006, 11:12 am
NAPCO PCI MINI June 18, 2005, 8:07 pm
NAPCO NETLINK NL-MOD June 20, 2005, 10:28 am
Napco HA eprom version November 28, 2005, 11:19 pm
Napco Developer Info August 5, 2006, 10:10 am
Napco Gemini Developer Protocol? March 3, 2005, 10:56 am
Napco-Gem-P3200 - Automation Interface March 15, 2005, 7:57 am
Napco P9600 Technical Question January 18, 2006, 10:58 am
Tying in GEM-X10 into Napco Gemini 816 Alarm System Controller March 6, 2007, 11:49 am
Napco Gemini GEM-P816 Program User Codes with GEM-RP3DGTL April 14, 2005, 3:07 pm
Elk M1 panel? June 30, 2005, 7:24 pm
Help please with panel spec April 14, 2005, 4:22 am
A-Bus and Futuresmart panel November 30, 2005, 6:40 pm
Using CAT 6 for speakers in a patch panel April 28, 2005, 2:54 pm