Changing Breaker Box - Looking for Different Perspective emilio_estevez 05-05-08
Posted by emilio_estevez on May 5, 2008, 2:21 pm
Please log in for more thread options
My question came up when a friend of mine asked if I could change out
his Federal Pacific breaker box to a newer, safer one. My background
is in industrial controls and I don't normally deal with power at the
service level. I only have about two years experience so as I am now
trying to learn more on my own, I'm finding a lot of things that don't
add up.

I started by doing some research to see what it would take to change
out a breaker panel in a house without turning off the service power.
It seems to me that it would not be any different getting shocked by
one of the mains than it would be to get shocked by the 120V at an
outlet. Each incoming line is 120V to ground (the same as the power
at a receptacle) and my body's resistance to ground would be roughly
the same. And according to Ohm's Law, the current that would go
through my body would be the same. I don't understand the difference.

Now obviously I don't plan on attempting this if the risk is actually
as serious as i've read, and I do realize that even very low voltages
can kill you if the current is high enough (would normally have to
break through the skin and into the blood stream where resistance is
very low), but the question still remains. Am I missing something?
I've read that if you touch either incoming service line that you will
most certainly die. Is that just to scare people that don't know
enough about what they're doing into hiring someone?

Lastly, I would like to point out that I work on a regular basis
around 480V / 240V and am quite frankly, scared of being shocked, and
I take every precaution available (which normally entails shutting off
the power at its source) before working around any live circuits. I
also understand that even 120V can definately be deadly, even at a
receptacle. I only used that as an example because I know people will
often change them without killing power.

I'd like to leave this topic as purely hypothetical. Simply an
example to learn from.


Thanks.

Posted by Tim Wescott on May 5, 2008, 3:06 pm
Please log in for more thread options
emilio_estevez wrote:
> My question came up when a friend of mine asked if I could change out
> his Federal Pacific breaker box to a newer, safer one. My background
> is in industrial controls and I don't normally deal with power at the
> service level. I only have about two years experience so as I am now
> trying to learn more on my own, I'm finding a lot of things that don't
> add up.
>
> I started by doing some research to see what it would take to change
> out a breaker panel in a house without turning off the service power.
> It seems to me that it would not be any different getting shocked by
> one of the mains than it would be to get shocked by the 120V at an
> outlet. Each incoming line is 120V to ground (the same as the power
> at a receptacle) and my body's resistance to ground would be roughly
> the same. And according to Ohm's Law, the current that would go
> through my body would be the same. I don't understand the difference.
>
> Now obviously I don't plan on attempting this if the risk is actually
> as serious as i've read, and I do realize that even very low voltages
> can kill you if the current is high enough (would normally have to
> break through the skin and into the blood stream where resistance is
> very low), but the question still remains. Am I missing something?
> I've read that if you touch either incoming service line that you will
> most certainly die. Is that just to scare people that don't know
> enough about what they're doing into hiring someone?
>
> Lastly, I would like to point out that I work on a regular basis
> around 480V / 240V and am quite frankly, scared of being shocked, and
> I take every precaution available (which normally entails shutting off
> the power at its source) before working around any live circuits. I
> also understand that even 120V can definately be deadly, even at a
> receptacle. I only used that as an example because I know people will
> often change them without killing power.
>
> I'd like to leave this topic as purely hypothetical. Simply an
> example to learn from.

_I_ turn the power off when I'm working around 120V. It won't always
kill you when you touch it, but I hate that tight feeling in my chest
for the hour or so after the 'event'.

Consider that when you're changing that 120V socket you're playing with
120V and ground on wires no bigger than 12 gauge, in a fairly well
controlled environment.

With the breaker box change, you're wrestling with 4 or 2 or 0 gauge
wires, the pair of which have 240V between them, which have to be
threaded out of one box, threaded into another, possibly trimmed and
certainly bent to new shapes. And what if they're six inches too short
and you need to run new ones? Add to that the fact that these wires are
fused for 100A or more, so even if you don't electrocute yourself you
run the risk of one hell of an arc if you short them together.

Me? I'll wimp out and call the power company to have the mains turned
off. And when they tell me they won't turn things back on without an
inspection I'll think of my homeowner's insurance and say 'yea verily
and thank you'.

--

Tim Wescott
Wescott Design Services
http://www.wescottdesign.com

Do you need to implement control loops in software?
"Applied Control Theory for Embedded Systems" gives you just what it says.
See details at http://www.wescottdesign.com/actfes/actfes.html

Posted by bud-- on May 6, 2008, 3:54 pm
Please log in for more thread options
emilio_estevez wrote:
> My question came up when a friend of mine asked if I could change out
> his Federal Pacific breaker box to a newer, safer one. My background
> is in industrial controls and I don't normally deal with power at the
> service level. I only have about two years experience so as I am now
> trying to learn more on my own, I'm finding a lot of things that don't
> add up.
>
> I started by doing some research to see what it would take to change
> out a breaker panel in a house without turning off the service power.
> It seems to me that it would not be any different getting shocked by
> one of the mains than it would be to get shocked by the 120V at an
> outlet. Each incoming line is 120V to ground (the same as the power
> at a receptacle) and my body's resistance to ground would be roughly
> the same. And according to Ohm's Law, the current that would go
> through my body would be the same. I don't understand the difference.
>
> Now obviously I don't plan on attempting this if the risk is actually
> as serious as i've read, and I do realize that even very low voltages
> can kill you if the current is high enough (would normally have to
> break through the skin and into the blood stream where resistance is
> very low), but the question still remains. Am I missing something?
> I've read that if you touch either incoming service line that you will
> most certainly die. Is that just to scare people that don't know
> enough about what they're doing into hiring someone?
>
> Lastly, I would like to point out that I work on a regular basis
> around 480V / 240V and am quite frankly, scared of being shocked, and
> I take every precaution available (which normally entails shutting off
> the power at its source) before working around any live circuits. I
> also understand that even 120V can definately be deadly, even at a
> receptacle. I only used that as an example because I know people will
> often change them without killing power.
>
> I'd like to leave this topic as purely hypothetical. Simply an
> example to learn from.

The hazard is not just shock. If you short the hot wire to hot, neutral,
or ground you will get a current of maybe 2,000A up to 10,000A. That
makes things like screwdrivers evaporate. Worse, they evaporate onto
your face. Added to the fun is that the transformer protection may allow
the fault current for an extended time. You -really- don't want to
change the panel with the wires 'hot'. If you work around 480 you should
have some familiarity with 'arc flash'.

An electrician might pull the meter. If you do, you have to be able to
be sure that kills the power. The utility company may take a real dim
view of cutting their seal on the meter. You better plan on telling
them, in advance.

And service panels have some unique features, like N-G bonding and
grounding electrodes. Also maybe aluminum wire.

Another problem is what you do if the wires are too short for the new
panel as Tim wrote.

I have read (but do not know) that Cuttler Hammer has replacement 'guts'
for FPE panels.

--
bud--

Posted by Dave on May 8, 2008, 3:04 pm
Please log in for more thread options

> My question came up when a friend of mine asked if I could change out
> his Federal Pacific breaker box to a newer, safer one. My background
> is in industrial controls and I don't normally deal with power at the
> service level. I only have about two years experience so as I am now
> trying to learn more on my own, I'm finding a lot of things that don't
> add up.
>
Dude, don't go there. Have you ever heard of anyone changing out their own
breaker panel, much less doing it live? No? Huh, wonder why that is?

The power that'll slam into you through 0 or 2 ga wire is HUGE and
UNFUSED... thousands of amps. The transformer on the pole has overload
protection, but it won't kick in until WAY after you're dead.

What you are considering is RIDICULOUSLY DANGEROUS. Trained professionals
don't do it.


Posted by Paul E. Schoen on May 9, 2008, 3:52 am
Please log in for more thread options

>
>> My question came up when a friend of mine asked if I could change out
>> his Federal Pacific breaker box to a newer, safer one. My background
>> is in industrial controls and I don't normally deal with power at the
>> service level. I only have about two years experience so as I am now
>> trying to learn more on my own, I'm finding a lot of things that don't
>> add up.
>>
> Dude, don't go there. Have you ever heard of anyone changing out their
> own breaker panel, much less doing it live? No? Huh, wonder why that
> is?
>
> The power that'll slam into you through 0 or 2 ga wire is HUGE and
> UNFUSED... thousands of amps. The transformer on the pole has overload
> protection, but it won't kick in until WAY after you're dead.
>
> What you are considering is RIDICULOUSLY DANGEROUS. Trained
> professionals don't do it.

You are right about that. The transformer is only fused at the primary to
protect it from overloads and malfunction, and many of these "pole pigs"
are 50 kVA or more. This means that a 120 VAC line to neutral or earth
current of 500 amperes would just start to make the fuse notice, and the
instantaneous current could be as high as 5000 amps (half a MegaWatt) for a
few cycles. Certainly enough to create a huge fireball and hurl globs of
molten copper and steel at the unfortunate amateur electrician who just
happened to let a scredriver slip across the mains.

A friend was working with another experienced test technician, doing
routine breaker testing in a large facility. Most of the switchgear was
disconnected, but the other test technician had to do some work in the main
fuse box, which I think was a 480 VAC feeder with heavy bus bar, probably
rated at 2000 amps or more. I think he had to tighten a bolt, and normally
he would have used a wrench that was mostly insulated with rubber tape, but
he was probably tired and in a hurry, and somehow the wrench slipped and
landed across the live bus. My friend saw it happen, and turned to the side
just as the fireball erupted, and it burned much of his face and body. The
technician who was responsible was badly burned, and soon died from his
injuries.

Here is a website with some images and movies of actual electrical arc
blasts so you can see the "potential" for danger:
http://205.243.100.155/frames/longarc.htm. Note that one of them is "only"
480 VAC.

Actually, I changed out the old breaker box in the house where I now live,
but I was completely remodeling it, and I had the utility company come out
and pull the meter. I had a separate feeder from my other house next door,
so I could provide temporary power. I actually located the new box on the
other side of the wall, next to the meter, inside an enclosed porch, and I
routed the 100 amp service cable into the new box while it was totally
dead. Even so, I treated it with respect, and I taped the exposed
conductors while I relocated them, and removed the tape only when I could
safely connect them to the main 100 amp breaker. It was several years later
that I was able to finish the bulk of the work, and I was able to have BGE
come out and replace the meter. I had tested the installation beforehand by
patching the other supply onto the mains, and I checked carefully for any
loose strands of the incoming service cable. Even so, I was a bit nervous
when the meter was reinstalled, but at least I had a main breaker directly
on the incoming line. The old breaker box did not have a main breaker.

More information and videos: http://www.lanl.gov/safety/electrical/

Paul







Similar ThreadsPosted
Changing Breaker Box - Looking for Different Perspective May 5, 2008, 2:21 pm
breaker schematic symbol June 21, 2006, 12:34 pm
Bought a house with a Fuse Box. Should I replace with a Circuit Breaker? February 18, 2005, 1:27 pm
changing DC voltage August 23, 2004, 6:56 pm
changing my VMeter from 0.25A to 25A September 8, 2004, 1:15 pm
Changing DC voltage May 15, 2006, 7:13 pm
color changing led problem October 17, 2004, 4:00 pm
changing wire gauge November 8, 2004, 2:39 am
Changing direction of an AC motor using relays July 5, 2006, 11:21 pm
Changing photo resistor resistance range. April 22, 2005, 3:15 pm
Q: Modding piezo in smoke detector - changing FREQ, AMP, or SHAPE? August 18, 2008, 4:47 am
Housekeeping is an interesting job or career where things are always changing, and even though you may work in a less than clean environment, you are required to always look clean and professional. Having appropriate housekeeping uniforms, dresses, or April 26, 2008, 3:51 am