Please log in for more thread options >>I'm looking at the AMP LightCrimp Plus No Polish system. Anyone care to
>>share the Pro's and Con's? I like my AMP modular plug crimper. That is >>why I >>am looking at AMP. But any other suggestions are welcome. I have been >>using >>the Leviton ThreadLock system. My problem is I only have about 1 fiber >>job a >>year. And even then it is usually only 12 to 24 terminations. I have a >>slow >>start with my polishing technique which smoothes out by the end of the >>job. >>Then the next fiber job comes along and I'm back to square one. :-)) >
> > Crimp-style connectors like AMP's LightCrimp and UniCam by Corning, as > well as the clones (these guys OEM manufacture for everyone and their > brother) are best suited for repair work, not the new installs. I know > that this may not go too well with every installer you are talking to > because on our side of the fence installation time is (almost always) all > the matters. But the reality of the thing is: you are inserting two > additional mechanical splices on every fiber, and that may be especially > bad on singlemode cables. And also reliability and couple other issues > below. > > Reliability of the crimp-style connectors also leaves to desire more. They > are notorious for not allowing ANY touching after the install is done. > With polished connectors (hot melts or regular epoxy or any other type of > glue, does not matter) your fiber is glued into the ferrule to the point > that, when pulling on the fiber, you will cut your fingers easier than > separating the fiber from the ferrule. In crimp style connector it's a, > well, crimped (or just rotated) plastic part that holds the whole thing > together. Any light pull on the fiber may potentially separate the fiber > from the connector, which destroys the link. Sometimes accidental pulls on > fiber are unavoidable, especially if you are working in a densely > populated shelf, and dressing your fibers in. While the potential is there, I'm going to have to disagree with the reality. Of the couple thousand LightCrimps I've installed, not one that was properly inserted (yes there were a few that didn't get right the first time) not one has pulled out with "light pull". In fact, one of my tests was to hold the fiber about 6 inches back and let the connector dangle. Then I'd give the connector a little tug. Never a problem. In the dense shelf situation, I think that you are more likely to break the glass behind the boot than pull it out of a crimp connector. And that happens with any type of termination. As for single mode, I'd fusion splice pigtails if I didn't want to puck-n-polish. >
> Yield: it is possible on a nice day to produce 100% yield with epoxy > polished connectors. It is impossible on a sizable crimp-style job NOT to > waste quite a few connectors because the cleaving stage is so important, > and you have no control over it, and by the time you realize something > went wrong, it's to late to redo the connector. There have been some > improvements made by Corning with introducing a base station with light > injector that makes it possible to judge be the amount of light that > escapes whether or not the cleave was done right, but you really have to > train your eye before you can tell. I would also say that yield is probably equal between the different styles especially if you are doing less than 100 terminations a year. Practice is critical. >
> Environment should also be considered when picking a particular type of > connector: if you are forced to work during construction phase (should be > avoided at all costs, but not always possible), the dust in the air may > not allow you to do good polishing. In this case the crimp style > connectors will do much better. If you have to work in a relatively clean > environment, and the number of connectors if considerable, you better of > doing polished style. > > Choose the style that suits the particular situation best and be prepared > to work with both technologies. I agree completely with being ready to do both. I've been thinking about fiber to the desk situations, (which we have here) that it's got to be much easier to do installs with pre-polished connectors than lugging a hot melt kit all over a building! >
> Good luck! > | ||||||||||||||||||||||||||||||||||||||||||||||
|
Posted by Perkowski on January 28, 2005, 3:13 pm
Please log in for more thread options > Dmitri(Cabling-Design.com) wrote:
> >> Alan Rench wrote:
>> >> >> >>> I'm looking at the AMP LightCrimp Plus No Polish system. Anyone care to
>>> share the Pro's and Con's? I like my AMP modular plug crimper. That is >>> why I >>> am looking at AMP. But any other suggestions are welcome. I have been >>> using >>> the Leviton ThreadLock system. My problem is I only have about 1 fiber >>> job a >>> year. And even then it is usually only 12 to 24 terminations. I have a >>> slow >>> start with my polishing technique which smoothes out by the end of the >>> job. >>> Then the next fiber job comes along and I'm back to square one. :-)) >>
>> >> >> Crimp-style connectors like AMP's LightCrimp and UniCam by Corning, as >> well as the clones (these guys OEM manufacture for everyone and their >> brother) are best suited for repair work, not the new installs. I know >> that this may not go too well with every installer you are talking to >> because on our side of the fence installation time is (almost always) all >> the matters. But the reality of the thing is: you are inserting two >> additional mechanical splices on every fiber, and that may be especially >> bad on singlemode cables. And also reliability and couple other issues >> below. >> >> Reliability of the crimp-style connectors also leaves to desire more. >> They >> are notorious for not allowing ANY touching after the install is done. >> With polished connectors (hot melts or regular epoxy or any other type of >> glue, does not matter) your fiber is glued into the ferrule to the point >> that, when pulling on the fiber, you will cut your fingers easier than >> separating the fiber from the ferrule. In crimp style connector it's a, >> well, crimped (or just rotated) plastic part that holds the whole thing >> together. Any light pull on the fiber may potentially separate the fiber >> from the connector, which destroys the link. Sometimes accidental >> pulls on >> fiber are unavoidable, especially if you are working in a densely >> populated shelf, and dressing your fibers in. >
> > While the potential is there, I'm going to have to disagree with the > reality. Of the couple thousand LightCrimps I've installed, not one > that was properly inserted (yes there were a few that didn't get right > the first time) not one has pulled out with "light pull". In fact, one > of my tests was to hold the fiber about 6 inches back and let the > connector dangle. Then I'd give the connector a little tug. Never a > problem. In the dense shelf situation, I think that you are more likely > to break the glass behind the boot than pull it out of a crimp > connector. And that happens with any type of termination. As for > single mode, I'd fusion splice pigtails if I didn't want to puck-n-polish. > >>
>> Yield: it is possible on a nice day to produce 100% yield with epoxy >> polished connectors. It is impossible on a sizable crimp-style job NOT to >> waste quite a few connectors because the cleaving stage is so important, >> and you have no control over it, and by the time you realize something >> went wrong, it's to late to redo the connector. There have been some >> improvements made by Corning with introducing a base station with light >> injector that makes it possible to judge be the amount of light that >> escapes whether or not the cleave was done right, but you really have to >> train your eye before you can tell. >
> > I would also say that yield is probably equal between the different > styles especially if you are doing less than 100 terminations a year. > Practice is critical. > >>
>> Environment should also be considered when picking a particular type of >> connector: if you are forced to work during construction phase (should be >> avoided at all costs, but not always possible), the dust in the air may >> not allow you to do good polishing. In this case the crimp style >> connectors will do much better. If you have to work in a relatively clean >> environment, and the number of connectors if considerable, you better of >> doing polished style. >> >> Choose the style that suits the particular situation best and be prepared >> to work with both technologies. >
> > I agree completely with being ready to do both. I've been thinking > about fiber to the desk situations, (which we have here) that it's got > to be much easier to do installs with pre-polished connectors than > lugging a hot melt kit all over a building! > >>
I agree. If you do a lot of Fiber got get a hotmelt kit, but, if you
>> Good luck! >> only have a few jobs every year Id stick with the AMP Lightcrimp system. I own it and I love it. PS. AMP and other manufacturers have already stated the future in premise fiber is the mechanical connector. Also, even though there are extra splices within the connector, youd have to be commander data to notice a fe dbs of extra loss. | ||||||||||||||||||||||||||||||||||||||||||||||
|
Posted by Dmitri(Cabling-Design.com on January 28, 2005, 6:14 pm
Please log in for more thread options jtodd5 dot 1 wrote:
> While the potential is there, I'm going to have to disagree with the
> reality. Of the couple thousand LightCrimps I've installed, not one > that > was properly inserted (yes there were a few that didn't get right the > first > time) not one has pulled out with "light pull". In fact, one > of my tests > was to hold the fiber about 6 inches back and let the connector dangle. > Then I'd give the connector a little tug. Never a problem. Don't have enough experience with LightCrimps to comment on the above, but I would never do it to UniCam. In my experience it is hard to quantify a "light tug", and it can easily become too much for the little part that holds the fiber in place. I think the spec says the connector can withstand 10N (approx 1kg or 2 pounds) of force, but it would be a steady force in my opinion. Your impulse momentum can easily exceed couple times that with a simple clumsy move of one finger. > In the
> dense > shelf situation, I think that you are more likely to break the glass > behind > the boot than pull it out of a crimp connector. And that happens with > any > type of termination. Well, you'd have to over-bend the fiber pretty badly for that to happen. In my experience accidental pulls on the fiber are MUCH more common. Example: you are re-connecting a connector that did not pass on the first round of tests, and you had to clean it. You're removing your hand from the shelf and a fiber gets under your wrist watch or something as silly as that. So, whereas both type are prone to breakage from over-bending, only crimp-style is prone to damage by pulling, which reduces the number of fatalities. > As for single mode, I'd fusion splice pigtails if
> I didn't want to puck-n-polish. You don't always get a luxury of having enough space for the splice trays, so there will be plenty of situations where you need to terminate directly on fiber. One of such situations: if you don't have a fusion splicer. > I agree completely with being ready to do both. I've been thinking
> about > fiber to the desk situations, (which we have here) that it's got to be > much > easier to do installs with pre-polished connectors than lugging a hot > melt > kit all over a building! You don't really have to have an oven, just carry anaerobic glue with you if you are not stationary. -- Dmitri Abaimov, RCDD http://www.cabling-design.com Cabling Forum, color codes, pinouts and other useful resources for premises cabling users and pros http://www.cabling-design.com/homecabling Residential Cabling Guide ------------------------------------- ##-----------------------------------------------## Article posted with Cabling-Design.com Newsgroup Archive http://www.cabling-design.com/forums no-spam read and post WWW interface to your favorite newsgroup - comp.dcom.cabling - 1153 messages and counting! ##-----------------------------------------------## | ||||||||||||||||||||||||||||||||||||||||||||||
|
Posted by Charlie on January 28, 2005, 5:02 pm
Please log in for more thread options We use only the Corning Unicam system and have terminated hundreds of
strands of single-mode fiber. The terminations are about $25 Canadian because we get end-user price as a university. We recently improved our results by getting the adapter that allows us to have a "ruby red" visual fault locator on the connector while crimping. The connector has a plastic collar that shows light if the fiber is not butted up properly to the stub. Charlie > I'm looking at the AMP LightCrimp Plus No Polish system. Anyone care to
I
> share the Pro's and Con's? I like my AMP modular plug crimper. That is why > am looking at AMP. But any other suggestions are welcome. I have been
using
> the Leviton ThreadLock system. My problem is I only have about 1 fiber job
a
> year. And even then it is usually only 12 to 24 terminations. I have a
slow
> start with my polishing technique which smoothes out by the end of the
job.
> Then the next fiber job comes along and I'm back to square one. :-))
> > | ||||||||||||||||||||||||||||||||||||||||||||||
| Similar Threads | Posted |
| No polish Fiber terminations? | January 27, 2005, 1:28 am |
| Terminations | August 28, 2007, 3:21 pm |
| patch panel terminations.. | March 12, 2006, 8:07 pm |
| Speaking of Patch Panel Terminations.. | September 10, 2005, 10:21 am |
| Supply Rack Mount Fiber Enclosures,Rack Mount Fiber Patch Panels,Rack Mount Terminal Panels | April 9, 2006, 11:44 am |
| Fiber Distribution Frames,Fiber Optic Distribution Frames | January 12, 2007, 11:10 am |
| Fiber for less | February 7, 2008, 12:22 pm |
| 10-Gig fiber color | August 16, 2004, 6:23 pm |
| Fiber question | November 16, 2004, 6:24 pm |
| fiber help needed please. | September 8, 2004, 1:47 pm |
| Fiber termination | October 15, 2004, 10:20 pm |
| Which Fiber Switch | February 23, 2005, 10:45 am |
| Fiber looping | January 14, 2006, 2:39 am |
| multimode fiber + GBIC | January 14, 2005, 11:43 pm |
| Fiber to the home - What are the standards ? | February 25, 2005, 8:26 pm |

No polish Fiber terminations?
Yahoo!
Windows Live
del.icio.us
digg
Netscape 








>
>
>