I'm looking at putting in an ethernet STP instalation for our factory
but i know that the shield should not be connected at both ends to
prevent ground loops (especially in our case: big motors, big power,
long distances). I'm concerned standard UTP will be overwhelmed by
electrical noise.

I plan to setup a STP patch panel in the control room, with the cables
sheild grounded there. Cables will run out from the panel to each
machine's control cabinet and connect to the equipment inside. So i
have a couple of questions:

First, i'm worried if the computer inside the machines control box has
a metal RJ45 jack, if i connect a sheilded patch cable i might end up
with fireworks as this will be grounding both ends (the equipment i
presume will be grounding the case of its RJ45 jack to its ground). Is
this a correct presumption or do electrical equipment isolate their
RJ45 jack from their ground?

Second, if the first case is true, can i get RJ45 connectors which can
crimp onto STP cable (im thinking of plastic isolated ones as in my
first point), or would i be better off putting a socket/plate in the
control box and running a patch lead from the plate to the equipment?

Many thanks,

Chris


Posted by Robert Redelmeier on July 25, 2006, 2:04 pm
Please log in for more thread options


g18c@hotmail.com wrote in part:
> I'm looking at putting in an ethernet STP instalation for our
> factory but i know that the shield should not be connected
> at both ends to prevent ground loops (especially in our
> case: big motors, big power, long distances). I'm concerned
> standard UTP will be overwhelmed by electrical noise.

Your concern is common and not unreasonable. But perhaps
excessive if those are constant load/speed motors. The EMI
they generate is strong, but too low a frequency to trouble
ethernet. OTOH, quickly variable loads or HF components like
from arc welders or X-Ray are probably worse.

Still, going ahead with STP is probably good insurance.

> First, i'm worried if the computer inside the machines control
> box has a metal RJ45 jack, if i connect a sheilded patch cable
> i might end up with fireworks as this will be grounding both
> ends (the equipment i presume will be grounding the case of its
> RJ45 jack to its ground). Is this a correct presumption or do
> electrical equipment isolate their RJ45 jack from their ground?

I would hope isolated, but only the mfr knows for sure.
I've seen ethernet cards both ways.

> Second, if the first case is true, can i get RJ45 connectors
> which can crimp onto STP cable (im thinking of plastic
> isolated ones as in my first point), or would i be better
> off putting a socket/plate in the control box and running
> a patch lead from the plate to the equipment?

You could probably squish an STP into a standard plug, but you
should not want to do this. Your STP runs should be terminated near
the equipment with a jack mounted on as solid and vibration-free
permanent structure as you can find. Then run a patchcord to
the equipment. It can take movement and vibration much better.

Rather than leave the far end of the shield dangling,
you could ground it through a resistor or capacitor.

-- Robert



Posted by on July 26, 2006, 1:42 am
Please log in for more thread options


Thanks for the reply Robert.

> Rather than leave the far end of the shield dangling,
> you could ground it through a resistor or capacitor.

Ok, i like the sound of a capacitor as it will block the current from
any ground loop static voltage. What would be a sensible value that is
typically used in such high noise environments? Would it be sensible to
put a resistor in series with a cap for safety (incase the cap failed
and shorted)?

Thanks,

Chris


Posted by Robert Redelmeier on July 27, 2006, 9:22 pm
Please log in for more thread options


g18c@hotmail.com wrote in part:
> Ok, i like the sound of a capacitor as it will block the
> current from any ground loop static voltage. What would be
> a sensible value that is typically used in such high noise
> environments? Would it be sensible to put a resistor in series
> with a cap for safety (incase the cap failed and shorted)?

I wouldn't bother. Caps usually fail open. Any fail closed
is very short lived :) But if you must, something reasonable
like 50-100ohms. For the cap, I'd use something with very low
ESR like tantalums. Electrolytics are right out.

-- Robert



Similar ThreadsPosted
Ethernet STP Patch in STP installation July 25, 2006, 9:38 am
Connecting an ADSL gateway to an ethernet port that connects to a patch panel July 14, 2006, 5:00 pm
Problem in Cable installation June 5, 2005, 2:15 am
CATV design and installation links June 4, 2005, 3:12 am
Need telephone cable installation troubleshooting advice October 31, 2005, 4:42 am
Instruction for Leviton 1x9 Bridged Telephone Distribution Module installation January 18, 2007, 11:47 pm
Sell Cat5e Modular Patch Panels,AMP Network Modular Patch Panels,Panduit Patch Panels,Mini-Com Shielded Modular Patch Panels March 15, 2006, 8:28 am
Long patch cables vs. patch panel August 18, 2004, 9:21 pm
Sell Cat5e FTP Patch Panels,Cat 5e FTP Patch Panels,Cat5e Shieldes Patch Panels March 15, 2006, 8:23 am
DIY Ethernet September 10, 2004, 8:57 pm
Patch Panels December 21, 2004, 8:30 pm
Ethernet cabling used outside July 29, 2004, 7:57 pm
Cat 5 for phone and ethernet? December 20, 2004, 9:57 pm
Cat 5 for phone and ethernet? December 20, 2004, 9:56 pm
PoE and Ethernet switches October 1, 2005, 10:22 am