Posted by Smowk on March 5, 2005, 10:25 am
Please log in for more thread options


anybody have any experience with cat6 and 440 volt power lines. we've run
parallel to them for a while and everything works perfectly. i thought you
werent supposed to do this?

smowk


Posted by James Knott on March 5, 2005, 5:06 pm
Please log in for more thread options


Smowk wrote:

> anybody have any experience with cat6 and 440 volt power lines.  we've run
> parallel to them for a while and everything works perfectly.  i thought
> you werent supposed to do this?
>

It's a bad idea, because you can induce enough voltage in the wires, to
cause a hazard. It generally won't bother the NICs though, as the
frequencies used to carry the data are well above those used for power and
they're also supposed to be able to withstand several hundred volts,
without creating a safety hazard. Now if you were to touch the cat6
conductors, while also touching some grounded metal, you might see why
you're not supposed to do that.



Posted by Al Dykes on March 5, 2005, 5:17 pm
Please log in for more thread options


>Smowk wrote:
>
>> anybody have any experience with cat6 and 440 volt power lines.  we've run
>> parallel to them for a while and everything works perfectly.  i thought
>> you werent supposed to do this?
>>
>
>It's a bad idea, because you can induce enough voltage in the wires, to
>cause a hazard. It generally won't bother the NICs though, as the
>frequencies used to carry the data are well above those used for power and
>they're also supposed to be able to withstand several hundred volts,
>without creating a safety hazard. Now if you were to touch the cat6
>conductors, while also touching some grounded metal, you might see why
>you're not supposed to do that.
>


How does anything get induced into the CAT5/5e/6 wire? The pairs are
twisted and carefully balanced to meet CATx specs and certification.
When CAT3 was new there was lots of discussion about EMI and if any
was found it was only in the most extreme situations. One way CAT5e
wire differs from CAT3 is carefull symetric twists, which cancel out
induced currents from external magnetic fields.

For that matter, for the OP, 440 volts is a "don't care" or even a
plus since it halves the amperage and it's amps, not volts that create
a magnetic field.

IMO Follow construction codes and be happy.

--

a d y k e s @ p a n i x . c o m

Don't blame me. I voted for Gore.


Posted by James Knott on March 5, 2005, 7:26 pm
Please log in for more thread options


Al Dykes wrote:

> How does anything get induced into the CAT5/5e/6 wire? The pairs are
> twisted and carefully balanced to meet CATx specs and certification.
> When CAT3 was new there was lots of discussion about EMI and if any
> was found it was only in the most extreme situations. One way CAT5e
> wire differs from CAT3 is carefull symetric twists, which cancel out
> induced currents from external magnetic fields.
>
> For that matter, for the OP, 440 volts is a "don't care" or even a
> plus since it halves the amperage and it's amps, not volts that create
> a magnetic field.

There's both common mode and differential mode coupling. Twisted pairs
reduce only the differntial mode coupling. As for coupling, there's both
inductive and capacitive coupling between the power and lan cables. There
will be some of both.



Posted by Al Dykes on March 5, 2005, 8:18 pm
Please log in for more thread options


>Al Dykes wrote:
>
>> How does anything get induced into the CAT5/5e/6 wire? The pairs are
>> twisted and carefully balanced to meet CATx specs and certification.
>> When CAT3 was new there was lots of discussion about EMI and if any
>> was found it was only in the most extreme situations. One way CAT5e
>> wire differs from CAT3 is carefull symetric twists, which cancel out
>> induced currents from external magnetic fields.
>>
>> For that matter, for the OP, 440 volts is a "don't care" or even a
>> plus since it halves the amperage and it's amps, not volts that create
>> a magnetic field.
>
>There's both common mode and differential mode coupling. Twisted pairs
>reduce only the differntial mode coupling. As for coupling, there's both
>inductive and capacitive coupling between the power and lan cables. There
>will be some of both.
>


Small amounts of common mode currents/volatges are blocked by the
transformers used to couple the cable to the circuity.

This document is interesting. (The text I've quoted is about 3/4 down)

My reading of the document says that in the normal home/office/light
manufacturing environment EMI is a non-issue with an ethernet plant
built to proper CAT5/5e spec and proper grounding of the hubs,
switches and computers. The Allen-Bradley paper also addresses heavy
industry applications where I imagine the ground currents could make
common mode issues interesting.

Shielded cable comes off worse than UTP.

http://www.ab.com/networks/enetpaper.html

"Testing was performed on a system where the communications
conductors (four-pair Ethernet cables) were placed in wire
ladder-ways. These cables were placed along side conductors
carrying 480 V drive-control voltages connecting the controller
and a high-horsepower motor. The differential voltage coupled
into the Ethernet cables varied, depending on the type of cable
tested.

The picture in Figure 12 shows the cable routing with respect to
the drive conductors. Table 3 shows the differential voltages
measured on the communications cables. The additional CMRR is
referenced to the shielded cable. The shielded cable is used as a
reference because this cable provides adequate performance in
environmental testing for Ethernet modules.

It is worth noting that there were no physical layer
communications errors during this sequence of testing"
[....]
"The four-pair Ethernet cables were tightly strapped to the
high-current secondary of the welding conductors and routed in
close proximity to the weld tip. This setup provided both
magnetic and radiated noises during the welding event. Figure 13
shows the routing of the cables on the robot arm. A
telecommunications analyzer was used to generate 100Mbit NRZ data
that was sent to a pair of Fast Ethernet transceivers for
encoding and decoding into MLT3 type data. The telecommunications
analyzer provided bit-level error detection. The performance
statistics were recorded for each of the five cables
tested. Surprisingly, zero data errors were recorded for each of
the five cables tested during the welding events."

--

a d y k e s @ p a n i x . c o m

Don't blame me. I voted for Gore.


Similar ThreadsPosted
EMI & Cat5 March 5, 2005, 10:25 am
Two T1s on one Cat5? September 21, 2006, 10:54 am
Best Way To Bundle Cat5? January 17, 2006, 7:10 pm
Looking for retractable CAT5 July 19, 2006, 9:50 am
cat5 problem September 11, 2006, 8:45 pm
T-connections with Cat5 UTP? October 7, 2007, 4:57 pm
Average Length of Cat5 Run August 25, 2004, 10:21 am
Can I use somehow use CAT5 instead of COAX for SPDIF? October 11, 2004, 8:24 pm
10 base 2 vs. Cat5 speed...? February 24, 2005, 10:22 pm
2 voice lines in an cat5 env March 3, 2005, 5:13 am
cat5 and electrical fields April 7, 2005, 9:50 pm
Ordering Cat5 online April 10, 2005, 10:57 am
lengthening CAT5 cable September 22, 2005, 1:49 pm
CAT5 25 pair and 66M or 110 blocks December 26, 2005, 10:24 pm
Cat5 cabling supplies in Toronto? July 29, 2004, 4:52 pm