Posted by DeputyDawg on October 29, 2005, 10:48 pm
Please log in for more thread options Hooked up 3 windows to the same Zone. To get an NOT READY ALL 3 Windows have to be breached. How can I make it so that if only ONE is breached it would show NOT READY? I wired all 3 together and then onto the single wire running to the OMNI Pro II board. | |||||||||||||||||||
|
Posted by on October 29, 2005, 10:23 pm
Please log in for more thread options You'll need to wire them in series, no parallel. | |||||||||||||||||||
|
Posted by DeputyDawg on October 30, 2005, 5:18 pm
Please log in for more thread options
Thanks. It did the trick. ::: You'll need to wire them in series, no parallel. | |||||||||||||||||||
|
Posted by Flavio Silva on October 30, 2005, 4:05 am
Please log in for more thread options
**** Post for FREE via your newsreader at post.usenet.com **** Test Hooked up 3 windows to the same Zone. To get an NOT READY ALL 3 Windows have to be breached. How can I make it so that if only ONE is breached it would show NOT READY? I wired all 3 together and then onto the single wire running to the OMNI Pro II board. -=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-= *** Usenet.com - The #1 Usenet Newsgroup Service on The Planet! *** http://www.usenet.com Unlimited Download - 19 Seperate Servers - 90,000 groups - Uncensored -=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-= | |||||||||||||||||||
| Similar Threads | Posted |
| OMNI Pro II Zone Secure Issue | October 29, 2005, 10:48 pm |
| RC-80B Thermostat Issue! | November 28, 2005, 10:03 am |
| Energy Cost feature in Omni | July 10, 2005, 1:07 am |
| Energy Cost feature in Omni | July 10, 2005, 11:29 am |

OMNI Pro II Zone Secure Issue
Yahoo!
Windows Live
del.icio.us
digg
Netscape 